I need an electricians advice.

The #1 community for Gun Owners in Indiana

Member Benefits:

  • Fewer Ads!
  • Discuss all aspects of firearm ownership
  • Discuss anti-gun legislation
  • Buy, sell, and trade in the classified section
  • Chat with Local gun shops, ranges, trainers & other businesses
  • Discover free outdoor shooting areas
  • View up to date on firearm-related events
  • Share photos & video with other members
  • ...and so much more!
  • 68_F100

    Expert
    Rating - 93.9%
    31   2   0
    Nov 8, 2010
    809
    18
    North Salem
    OK here is what I am going to do. I am going to use a 30 amp breaker. Run 3 feet of 10/2 to a box with a twist lock receptacle. Then I am going to use about 3 feet of 10ga stranded wire with a twist lock plug on one end and crip lugs on the other to fit the screw terminals. Thats like a 6 foot run with a twist lock in the middle. Sound good?
     

    Mr Evilwrench

    Quantum Mechanic
    Emeritus
    Rating - 0%
    0   0   0
    Aug 18, 2011
    11,560
    63
    Carmel
    Wow, luxury; you're already right next to the breaker. I had to run about 25 feet to get to my outlet for the welders, but yeah, 30A and 10/3. Didn't worry about a twist lock since there's not really any motion and I'll always be right there when it's running :) My compressor is only 120V, but it has its own circuit, too.

    Voltage drop with wire to code will pretty much just soften the startup current a little, but the breaker will pop before the wire gets hot enough to ignite the insulation. Remember, as long as you haven't kinked the snot out of some spot, the voltage drop, and therefore the heat, will be distributed uniformly along the length of the wire. Run too long a wire, and you're not running a fire risk, just going to slow down the motor startup. Slow it down enough and the breaker might pop, but it still won't catch fire.
     